- Jun 18, 2009
- 77
I'm hoping to get some feedback regarding the footing design for houses on piers "Drive Unders". See attached plan. Basically we are designing 1 and 2 story houses on piers for a high wind load area. The piers are masonry and the floor system is wood framing.
Currently our foundation consist of shallow footings 3'x3' connected by grade beams. The grade beams are reinforced with rebar top and bottom and stirrups.
We have gotten a lot of push back from the contractors. The several contractors have mentioned that the standard for the area is to use a 24" wide continuous footing with 3-#5 bottom only. One contractor has even sent us plans from other engineers showing the 24" wide footing.
When I run the numbers, the moments on the grade beam from the lateral wind loads require top steel so I'm not sure how the other engineers are justifying their design.
Please note that the house in the attachment is one of the smaller houses. The houses can get much larger. Typical pier loads are approximately 10k axial and 2k lateral.
I look forward to your comments
Currently our foundation consist of shallow footings 3'x3' connected by grade beams. The grade beams are reinforced with rebar top and bottom and stirrups.
We have gotten a lot of push back from the contractors. The several contractors have mentioned that the standard for the area is to use a 24" wide continuous footing with 3-#5 bottom only. One contractor has even sent us plans from other engineers showing the 24" wide footing.
When I run the numbers, the moments on the grade beam from the lateral wind loads require top steel so I'm not sure how the other engineers are justifying their design.
Please note that the house in the attachment is one of the smaller houses. The houses can get much larger. Typical pier loads are approximately 10k axial and 2k lateral.
I look forward to your comments