I have spent my whole career as a structural engineer in Florida, mostly with low rise structures where this whole footing uplift deal is a big issue in design. I am relatively conservative as a structural engineer, but I see the two sides of this coin.
1. CODE:
I have argued there should be a small note added into the code to allow the use, at the discretion of the engineer of record, to use up to 100% (ok, maybe 90%) of the weight of an engineered slab and/or foundation.
But right now, if we are talking about what "code" says, I think they all say 0.6D or similar. And we all know how perfectly written codes are (tongue firmly implanted in cheek). Its been my understanding that the 0.6 dead factor is because the majority of dead loads have unpredictable weights that may change throughout the lifespan of a structure. A foundation of course does not fit this description, and thus in my opinion, it does not fit the intent of the 0.6 reduction. I do not believe you would violate the spirit of the code in this sense, for whatever that is worth I am not sure
2. PRACTICE
I have been fortunate to perform forensic investigations after Hurricanes Charlie, Jeanne, Francis, Katrina and several tornadoes. The only footing failure from uplift I saw was arguably a scour/storm surge failure, but a front porch post embeded in a small cube of concrete was probably about 50 feet from where it was built (on the bay in Biloxi). I have seen lots of roof failures, and structures ripped from the slab and foundation. Even a partial roof cladding failure will drastically reduce the uplift load getting down to a footing.
I think we are all not being realistic if we think that wind pressure in a one story building will pull a footing out of the ground by punching a whole in the slab. So the building envelope would be perfectly intact- roof, windows, doors, etc. which would allow the wind pressure to continue to keep increasing? And no element along the load path would fail prior to the foundation being literally pulled out of the ground? If this happens, we have bigger issues to deal with, like the survival of the species.
I guess that would be my argument for the code change to allow 0.9D for foundations and slabs....