So, today I was asked to review a report, observations, and photographs regarding a site visit to determine if a retaining wall, being constructed on a residential site, was being constructed according to the plans and current adopted building code. The engineering for the retaining wall was performed by a PE in our office who is no longer employed with our company.
As I am scrolling through the photos, I came across one where a worker was standing atop the formwork with a sprayer wand and a cloud of whatever he was spraying coming up out of the formwork. So, I called the inspector and asked just what was being sprayed. Form release agent is what I'm told. So I ask was the reinforcing already set and of course the answer was yes. Further questioning revealed that, at least for this particular wall contractor, it was common for the form release agent to be sprayed into the formwork after all the reinforcement set. This particular wall was only 10" thick so I can imagine ALL of the rebar was well coated.
What research I have been able to sift through has revealed that ACI 301 says form release agent should not be applied on to the reinforcement. Most manufacturers of form release agent, whose application instructions I have read, specifically warn against getting the product on the reinforcement and advise to coat the forms prior to installation. As I generally do not review residential retaining wall construction observations, I do not know how long this has been going on nor just how many retaining walls, and foundation walls for that matter, out there have been constructed in this manner.
I am trying to do as much research as I can before I stir the pot but, from what I have found so far, this is potentially a huge problem and a wide spread (locally anyway) issue.
Has anyone else run across this before? Are there any papers, publications, specs, etc, on this that I could read before I kick start this sh&$ storm?
As I am scrolling through the photos, I came across one where a worker was standing atop the formwork with a sprayer wand and a cloud of whatever he was spraying coming up out of the formwork. So, I called the inspector and asked just what was being sprayed. Form release agent is what I'm told. So I ask was the reinforcing already set and of course the answer was yes. Further questioning revealed that, at least for this particular wall contractor, it was common for the form release agent to be sprayed into the formwork after all the reinforcement set. This particular wall was only 10" thick so I can imagine ALL of the rebar was well coated.
What research I have been able to sift through has revealed that ACI 301 says form release agent should not be applied on to the reinforcement. Most manufacturers of form release agent, whose application instructions I have read, specifically warn against getting the product on the reinforcement and advise to coat the forms prior to installation. As I generally do not review residential retaining wall construction observations, I do not know how long this has been going on nor just how many retaining walls, and foundation walls for that matter, out there have been constructed in this manner.
I am trying to do as much research as I can before I stir the pot but, from what I have found so far, this is potentially a huge problem and a wide spread (locally anyway) issue.
Has anyone else run across this before? Are there any papers, publications, specs, etc, on this that I could read before I kick start this sh&$ storm?