With work the way it's been I've been getting more into inspections and am concerned about due deligence.
From NFPA #25 2002
12.6.2 Testing.
12.6.2.1* All backflow preventers installed in fire protection system piping shall be tested annually in accordance with the following:
(1) A forward flow test shall be conducted at the system demand, including hose stream demand, where hydrants or inside hose stations are located downstream of the backflow preventer.
(2) A backflow performance test, as required by the authority having jurisdiction, shall be conducted at the completion of the forward flow test.
This is a big deal especially in those areas of the country where it's never been enforced.
Some states, I'll single out South Carolina, require provisions be made for forward flow testing in new installaitons, but for others forward flow testing is overlooked by both code and fire officials.
Not a problem if there is a fire pump with test header downstream or there's fire hydrants downstream.
If provisions haven't been made, I envision something similar to a test header for fire pumps, annual forward testing can become a big undertaking in itself. Suppose we could turn FDC check valve around but in some systems this isn't so easy to do. In some places, a pit for example, this can become difficult to accomplish.
Georgia has adopted NFPA #25 but at the prices given for inspections it's clear few, if any, are actually doing this part of the inspection.
Question: What is happening in regards to foreward testing in your state and, if it is pushed, what have you been doing as far as connections?
Thanks.
From NFPA #25 2002
12.6.2 Testing.
12.6.2.1* All backflow preventers installed in fire protection system piping shall be tested annually in accordance with the following:
(1) A forward flow test shall be conducted at the system demand, including hose stream demand, where hydrants or inside hose stations are located downstream of the backflow preventer.
(2) A backflow performance test, as required by the authority having jurisdiction, shall be conducted at the completion of the forward flow test.
This is a big deal especially in those areas of the country where it's never been enforced.
Some states, I'll single out South Carolina, require provisions be made for forward flow testing in new installaitons, but for others forward flow testing is overlooked by both code and fire officials.
Not a problem if there is a fire pump with test header downstream or there's fire hydrants downstream.
If provisions haven't been made, I envision something similar to a test header for fire pumps, annual forward testing can become a big undertaking in itself. Suppose we could turn FDC check valve around but in some systems this isn't so easy to do. In some places, a pit for example, this can become difficult to accomplish.
Georgia has adopted NFPA #25 but at the prices given for inspections it's clear few, if any, are actually doing this part of the inspection.
Question: What is happening in regards to foreward testing in your state and, if it is pushed, what have you been doing as far as connections?