I am designing the foundation for a horizontal aboveground storage tank. It is supported by 2 saddles. My question is do I need to put a perimeter curtain wall down to frost, do I need to place well graded gravel down to frost or can I go with 18 inches of stone. Mat foundation is 12 inches thick and the frost line is 42"
Thanks
 
Replies continue below

Recommended for you

Place mat foundation below frost grade and use concrete walls to support the saddles.
Alternatively you could go high load insulation shallow foundation design method but really isn’t advisable. I always would recommend removing any soil in the frost line with clean crushed stone without fines, if the soil has moisture it’s going to heave frost wall or not.
 
Thank you. Do we need walls at the saddle or can we just add more rebar in the mat? Do you have a sketch?
 
Most of the cases I've seen, they had separate supports (footing + rectangular pier) under each saddle.
 