NFExp
Structural
- Jun 18, 2009
- 74
I have been working on foundation design for a 4-story wood frame multi-family design on a very high plastic soil. The geotech has given the following parameters for the soil.
Bearing pressure = 2500 psf
PTI Parmeters
Center em = 8.3', ym = -2.2"
Edge em = 5.1', ym = 1.8"
ks = 125pci
Differential Settlement = 1:15
The exterior loading on the wall is fairly light (3500plf).
The contractor is a decent sized company with a lot of local projects. The geotech and the contractor claim that all the projects they work on are a 5" slab with some conventional reinforcement and "top steel".
WE have designed the slab with 2 methods. Both designs are much more robust than the contractors experience. The first method we used is the PTI method, which gave us the following design (post tension 4" slab with 18" x 31" ribs at 8' on center or a 10" equivalent slab).
The 2nd method, we modeled the building in SAFE. In the model, we removed the outer 5' of soil supports in an attempt to model the "Center lift" condition. Our model cantilevers the building 5'. As you can imagine, in order to get the model to work, the slab becomes very large. Even with the large slab, at the corners and jogs, the bearing pressure is higher than allowable. We tried flat slabs and ribbed design. All our designs were either not practical or bearing pressure was exceeded.
My questions are as follows:
1.) Can we use the PTI method even though the PTI method does not consider corner and building jogs?
2.) Are these soil parameters compatible with a shallow foundation or is a deep foundation required?
3.) Is our Safe model too conservative?
FYI, we asked the geotech to confirm his numbers and he stood by his original report.
Thanks for your feedback.
Bearing pressure = 2500 psf
PTI Parmeters
Center em = 8.3', ym = -2.2"
Edge em = 5.1', ym = 1.8"
ks = 125pci
Differential Settlement = 1:15
The exterior loading on the wall is fairly light (3500plf).
The contractor is a decent sized company with a lot of local projects. The geotech and the contractor claim that all the projects they work on are a 5" slab with some conventional reinforcement and "top steel".
WE have designed the slab with 2 methods. Both designs are much more robust than the contractors experience. The first method we used is the PTI method, which gave us the following design (post tension 4" slab with 18" x 31" ribs at 8' on center or a 10" equivalent slab).
The 2nd method, we modeled the building in SAFE. In the model, we removed the outer 5' of soil supports in an attempt to model the "Center lift" condition. Our model cantilevers the building 5'. As you can imagine, in order to get the model to work, the slab becomes very large. Even with the large slab, at the corners and jogs, the bearing pressure is higher than allowable. We tried flat slabs and ribbed design. All our designs were either not practical or bearing pressure was exceeded.
My questions are as follows:
1.) Can we use the PTI method even though the PTI method does not consider corner and building jogs?
2.) Are these soil parameters compatible with a shallow foundation or is a deep foundation required?
3.) Is our Safe model too conservative?
FYI, we asked the geotech to confirm his numbers and he stood by his original report.
Thanks for your feedback.