What is the current code requirement for any reduction in foundation self-weight (D) when resisting wind uplift (W)?
2021 IBC contains the following verbiage:
"For load combinations that include the counteracting effects of dead and wind loads, only two-thirds of the minimum dead load likely to be in place during a design wind event shall be used."
In spite of this, there is no load combination shown that includes 0.67D.
In ASCE 7-16, combination 7 gives 0.6D + 0.6W. This is different from the two-thirds that IBC says.