Foundation underpinning with overpour - concrete not flowing far enough under the footing

Status
Not open for further replies.

Anton Polyakov

Computer
Jul 4, 2021
5
Good day experts

I am doing a foundation underpinning at my house with overpour method. The issue I am facing is that overpoured concrete only goes half way under the 16 inches wide footing leaving a 1.5-2 inch gap at the rear part between new slab and the footing.

I use proper vibrator and vibrated hell out of it. Concrete was pretty fluid. One suspicion I am thinking of is - maybe the pouring gap was not big enough and it didn't create enough hydro pressure for concrete to go all the way under the slab? It had like 2 inch opening between the bottom of the footing and vertical form where the inclined lip was (you can see on the photo).

IMG_5003_vd6bmo.jpg


Any other hints what I might be doing wrong? It's hard to find any guides/videos showing the process itself.



Thank you for your help!
 
Replies continue below

Recommended for you

Any good suggestions for superplastizer? I've been trying this one however honestly didn't notice too much difference in terms of fluidity in the field

Do I need to force pack the concrete under the footing with 2x4 or smth? I assume there's still a limit of how fat it can flow on its own
Does this depend on the hole size at all?
 
From what I have learned from PEinc over the time on this forum, dry pack is your friend.

(Disclaimer - I will await PEinc's comments/confirmation :))

All joking aside, you could pour concrete up to 4 inches below the footing base then dry pack the last 4 inches.

 
hey EireChch, so the overpour simply doesn't work or am I doing it wrong? I thought it's the latter hence trying to figure out what I am doing wrong

Some people say it might be the air trapped
 
It does need somewhere to vent the air. So that certainly is possible.
 
As EireChch said, drypack is your friend. Don't count on overpouring to provide full bearing under the existing footing. Pour the underpinning concrete to within 2.5 to 3 inches below the lowest bottom of the existing footing within the pier width being excavated. Then, install the drypack as a stiff, damp mixture of 2 parts sand to 1 part Portland cement. Ram the drypack hard into the gap a little at a time until the entire space between the footing and the underpinning pier is filled. Non-shrink and non-metallic drypack are not usually needed. Drypack the gap the day after the pier concrete has been poured.

 