XR250
Structural
- Jan 30, 2013
- 5,291
This is a project of mine where:
a) the contractor did not install any rebar in the wall
b) it was my understanding that the site was flat so there would be no meaningful retaining
c) not enough anchor bolts were installed
d) The top courses of the CMU were not grouted where they transitioned from 12 to 8 and from 8 to 6.
Below is my repair concept. Cut the face shells of the CMU sufficiently to be able to install the rebar and grout. That will take care of my retaining and give me something to resist the uplift with (approx 200 PLF). Somehow I need to tie the top 6" CMU to the rest of the mess to resolve the direct tension. Was thinking since they already have the face shells cut out, they could drill upwards into the 6" block and epoxy rebar into the underside. Alternatively they could drill down through the sill plate and the 6 inch block and try to epoxy rebar into the 8" CMU below. Add additional post-installed anchors as needed. None of this repair is ideal though.
Thoughts?
a) the contractor did not install any rebar in the wall
b) it was my understanding that the site was flat so there would be no meaningful retaining
c) not enough anchor bolts were installed
d) The top courses of the CMU were not grouted where they transitioned from 12 to 8 and from 8 to 6.
Below is my repair concept. Cut the face shells of the CMU sufficiently to be able to install the rebar and grout. That will take care of my retaining and give me something to resist the uplift with (approx 200 PLF). Somehow I need to tie the top 6" CMU to the rest of the mess to resolve the direct tension. Was thinking since they already have the face shells cut out, they could drill upwards into the 6" block and epoxy rebar into the underside. Alternatively they could drill down through the sill plate and the 6 inch block and try to epoxy rebar into the 8" CMU below. Add additional post-installed anchors as needed. None of this repair is ideal though.
Thoughts?