In a framed roof with a knee wall how can one determine the load from the roof through the wall to the floor.
If the point at which the knee wall touches the rafter Is taken as a support then basically half the roof load transfers but in reality only a part of the load is going to transfer based on the deflection of the rafters. This of course is assuming the rafters are designed to carry the load without the knee wall.
I normally design the rafters to carry the load in order to get the insulation required in our area. I call for 2x12’s. I then specify a gap between the knee wall and the rafters greater then the design calculated deflection. Then I only take the weight of the wall down to the floor framing.
In the rare occasion that I use smaller rafters and use the knee wall to support the rafters I take the reaction of the rafters at the knee wall and the weigh of the knee wall as a load on the floor joists.
My question is, “is there a way to determine the load based on the deflection of the rafter at the knee wall”?
If the point at which the knee wall touches the rafter Is taken as a support then basically half the roof load transfers but in reality only a part of the load is going to transfer based on the deflection of the rafters. This of course is assuming the rafters are designed to carry the load without the knee wall.
I normally design the rafters to carry the load in order to get the insulation required in our area. I call for 2x12’s. I then specify a gap between the knee wall and the rafters greater then the design calculated deflection. Then I only take the weight of the wall down to the floor framing.
In the rare occasion that I use smaller rafters and use the knee wall to support the rafters I take the reaction of the rafters at the knee wall and the weigh of the knee wall as a load on the floor joists.
My question is, “is there a way to determine the load based on the deflection of the rafter at the knee wall”?