Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Tek-Tips community for having the most helpful posts in the forums last week. Way to Go!

French drain help, cut waffle membrane

Status
Not open for further replies.

Tuna425

Electrical
Jul 30, 2015
1
0
0
US
I just had my French drains replaced in my basement.

Hired a guy to repair the walls that were cut and redo the tiles on the floor. My problem is that the idiot tile guy cut the waffle sheet at floor level all the way around the basement. So now all the weep holes are leaking onto the floor.

Can I just cut a gap along the wall and replace the cut sheets? Or would the seam cause leaks?

I really don't want to rip all that new work out
 
Replies continue below

Recommended for you

A side question for us. Why did you have to replace the French Drains? Plugged?

Many with your situation cut a wide slot in the floor, next to the wall to let seepage water get down to drains.

The real solution would be to install drains outside the footings (and properly filtered).

Sorry, but the term waffle sheet is not common here (Wisconsin). Explain.
 
I did a search on Google and come up with this as underlayment for floor tile. How does one replace a drain system under the floor without cutting the underlayment?

Perhaps a sketch of a cross section of the floor and walls might clear up things.
 
Status
Not open for further replies.
Back
Top