Friction Factor TAN ?

Status
Not open for further replies.

jagti

Civil/Environmental
Oct 17, 2009
28
What should be the Typical Friction Factor Value Modular Block wall resting over Granular Thickened Pad apparently Geo technical Engineer is asking me to use 0.35 which i think is overly conservative. My allowable friction angle for Engineered Thickened Granular Base is 36 Deg friction angle for Retained clear stone is 38 degrees Shouldn't i be using 0.67 X 36 deg=24 deg tan24:- 0.45.
If i use 0.35 Friction factor my Block Gravity wall fails in Base Sliding
He is kind of referring to Can Foundation Engineering Manual Table 24-4 page 382. Under Formed or pre-cast concrete coloum.

I want to convince him Modular Dry Cast Segmental Block falls under Mass Concrete or Masonry category in that table which relies on free draining material as backfill & base.

Help required in suggestions I am right in my approach.
 
Replies continue below

Recommended for you

I would say neither. For modular walls we typically use NCMA's segmental wall design manual, which takes the lowest value of:

For conventional (no reinforcing grid)
1. The block sliding across the granular base:
Weight * tan(phi for granular base say 40deg) * u
where u is a reduction coeficient for the smooth block surface typically equal to 0.7.

2. The sliding of the foundation soil:
Weight * tan(foundation soil say 28deg)

For grid with reinforcing grid:
1. The granular pad sliding
Weight * tan(leveling pad say 40deg)

2. The sliding of the foundation soil:
Weight * tan(foundation soil say 28deg)

3. The sliding of the reinforced soil:
Weight * tan(reinforced soil say 34deg)

Foundation controls = 0.53



EIT
 
Thanks Rfreund,

What if the Engineered Granular Pad friction angle is 36 deg so would that mean the Friction factor would be Tan32 X 0.7 = 0.5 or 0.67X Tan36=0.49 or 0.5 X Tan 36=0.36.

i.e which is the appropriate value to use for Delta/ Masonry reduction factor
 
If it were a gravity wall with no geogrid than I would use :

Tan(36)*0.7 for the block and pad
The u being a masonry reduction factor

I can reference the NCMA section on Monday if you'd like.

EIT
 