Hello,
Being a mechanical engineer with a civil technician for a father lead me to designing my own workshop.
It is a 32'x64' post and beam, single storey building designed to use the same bent (think large scale truss) every 8 ft in the long direction. The truss is suported on footings in a 6" slab on grade that runs the long direction of the building including one in the centre, such that the truss only spans 16 ft.
I live in a area where the design snow loading is 2.74kPa or about 40 psf. Our frost depth is 5 feet.
I used to ASCE design guide for frost protected foundations to design the correct insulation for the building. Basically ended up with R=10.5 which is about 3" of XPS on the derated ratings in the standard, and extending out 5 ft from the edge of the slab. The slab is 24" on the thickened perimeter and the central footing.
I approached a structure engineer to seek help on the selection of reinforcing and preparation of the pad. I had envisioned removing topsoil then leveling the site then adding 6-12" of non-frost suceptible fill compacted in 3 or 6" lifts. The soil is a firm clay till on top of a better draining gravel below.
After meeting with the engineer I'm told he has the reputation as the most conserevative local structure engineer. He has recommended so far doubling our fill and using a large Bomag type roller to compact it. He has also recommended 200 feet of french drain / interceptors around the perimeter.
He then interviewed me regarding the loads in the building, the largest being a 9000 lb farm tractor on quite large tires. He said he would be using this information to see if a thinner slab could be used.
Most garages in the area are built on 6" of 3/4" river stone / pea gravel with a 4" slab and nothing else. This meets the local building code.
I'm concerned there is maybe 3000$ of extra engineering going into saving 500$ on a truckload of cement. I'm also concerning I'm getting an expensive over designed slab to protect the engineer from liability. I told him cracking was acceptable for the end use, he replied it wasn't to him.
If I abandon plans of constructing post and beam, an engineer is not longer required by law to be involved with stamping drawings for the foundation. This is sort of silly as the outside footing loads are higher on a stick built shop with trusses spaning the 32'.
We also have available to us within 5 minute drive a sandpit with moderately coarse well draining sand with some fist sized rocks in it (say 2 per cubic ft). We have been trying to accomodate this in our design as it is nearly free for us and reduces trucking costs. The engineer says it is not suitable for anything we are doing.
Anyone have any comments for me, critism of my expectations welcome! Oh and he wants a soils test done. Am I out of line for being concerned with costs? To me this is a small slab.
Being a mechanical engineer with a civil technician for a father lead me to designing my own workshop.
It is a 32'x64' post and beam, single storey building designed to use the same bent (think large scale truss) every 8 ft in the long direction. The truss is suported on footings in a 6" slab on grade that runs the long direction of the building including one in the centre, such that the truss only spans 16 ft.
I live in a area where the design snow loading is 2.74kPa or about 40 psf. Our frost depth is 5 feet.
I used to ASCE design guide for frost protected foundations to design the correct insulation for the building. Basically ended up with R=10.5 which is about 3" of XPS on the derated ratings in the standard, and extending out 5 ft from the edge of the slab. The slab is 24" on the thickened perimeter and the central footing.
I approached a structure engineer to seek help on the selection of reinforcing and preparation of the pad. I had envisioned removing topsoil then leveling the site then adding 6-12" of non-frost suceptible fill compacted in 3 or 6" lifts. The soil is a firm clay till on top of a better draining gravel below.
After meeting with the engineer I'm told he has the reputation as the most conserevative local structure engineer. He has recommended so far doubling our fill and using a large Bomag type roller to compact it. He has also recommended 200 feet of french drain / interceptors around the perimeter.
He then interviewed me regarding the loads in the building, the largest being a 9000 lb farm tractor on quite large tires. He said he would be using this information to see if a thinner slab could be used.
Most garages in the area are built on 6" of 3/4" river stone / pea gravel with a 4" slab and nothing else. This meets the local building code.
I'm concerned there is maybe 3000$ of extra engineering going into saving 500$ on a truckload of cement. I'm also concerning I'm getting an expensive over designed slab to protect the engineer from liability. I told him cracking was acceptable for the end use, he replied it wasn't to him.
If I abandon plans of constructing post and beam, an engineer is not longer required by law to be involved with stamping drawings for the foundation. This is sort of silly as the outside footing loads are higher on a stick built shop with trusses spaning the 32'.
We also have available to us within 5 minute drive a sandpit with moderately coarse well draining sand with some fist sized rocks in it (say 2 per cubic ft). We have been trying to accomodate this in our design as it is nearly free for us and reduces trucking costs. The engineer says it is not suitable for anything we are doing.
Anyone have any comments for me, critism of my expectations welcome! Oh and he wants a soils test done. Am I out of line for being concerned with costs? To me this is a small slab.