Suggestion to cgap (Electrical) May 7, 2002 marked ///\\I am trying to determine the load being added to the electrical system - equipment states 200A Full Load and 25A Largest Motor
///NFPA 70-1999 National Electric Code in Art. 430-24 suggests to add 25% of the largest motor current, i.e. 200A + 0.25 x 25A=206.25A\\When a piece of equipment states "Full Load" Amps, is that the same as "Starting Amps" or "Running Amps"?
///Full-load amps = rated amps, see manufacturer's catalogs, e.g. Baldor, Reliance, etc.
Starting amps are close to inrush current and locked rotor amps if no voltage reduction is applied accross the motor terminals, e.g. a wye-delta starter.
Running amps can be full-load amps, greater than full load amps, if the motor has the service factor greater than one or lower than full load amps if the shaft load is smaller than the rated shaft horsepower.\\\