Full load current greater than nameplate value 1

Status
Not open for further replies.

Marcus750

Mechanical
Mar 27, 2019
5
I have a pump motor that is measuring 9A on full load and the nameplate value is 3A. I'm no doubt opening myself up for derision, but What does this mean?

Thanks
 
Replies continue below

Recommended for you

It doesn't seem possible to be honest as this is three times the rating and you would expect the motor to significantly overheat / burn / smoke.

Are you sure you're reading the right data? Sometimes you have different voltages / windings and hence different currents. A picture of the nameplate and what voltage and where you're measuring the voltage would help ( single phase, three phase, ??)

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Only other thing though is that for start up the load can go 4-6 times higher than Full load for a short period as it speeds up. That is quite normal.

Are those steady state operating readings?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
At 9A that's approaching locked rotor amp value. Has the viscocity of the material being pumped changed?
 
A motor which is mis-connected can run at very high slip with very high current if a motor design to operate in delta is wired in star (wye). Usually the overload proetction trips the motor - at 300% overload it should be tripping in about 30s - 40s or so.
 
Can you describe the start/stop cycles? How long does the pump run, and does it draw 9A continuosly? How long are the pauses between pumping actions?
 
Or tripped the overload...

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
 
Sadly Our OP is a two post master and last logged in to post the question.

Marcus - If you ever come back and read these responses if there is a next time please don't leave it so long...

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Hi All, Firstly a big thank you to all who replied to me query and apologies for the delay in responding as I was on holiday for to weeks. Initially when I had the pump on manual test it was displaying the aforementioned readings, but when I tested again it was tripping; so a fault with the motor. Looks like we're going to get a new LTHW pressurisation unit.

 