BearB
Electrical
- Jan 18, 2007
- 54
Where I am working they want to rebuild a Full Voltage non Reverse 2300v induction Motor Starter. I have not worked much with medium voltage starters and I am asking for assistance. We have several older 2300v Induction motor starters that have had the motors and equipment removed. I am going to use the control circuit and size components to the motor being installed. The control circuit is: 2 overloads controlled by 2 CT's and a GCT controlling a relay. Along with a start and stop switch that controls a 230vac relay and a contact from that entergises the main contactor. The current components are too old or undersized so they need sized to the motor being installed. The induction motor being installed is 450 hp, 2300v, 111 amps.
I was considering using 2 150/5 CT's, a Cutler-Hammer Vac. 400amp Contactor (because this device is available in our company store room. The 2300/230 transformer is in good shape and will be used. I need assistance sizing components. Are the CT's proper size?, What type of overload relays ? What type of ground fault CT and relay? contactor ok? Any assistance is appreciated.
I was considering using 2 150/5 CT's, a Cutler-Hammer Vac. 400amp Contactor (because this device is available in our company store room. The 2300/230 transformer is in good shape and will be used. I need assistance sizing components. Are the CT's proper size?, What type of overload relays ? What type of ground fault CT and relay? contactor ok? Any assistance is appreciated.