I am a new member to the site, but has always refer to the site for answer to many of my electrical related issues. Recently, I ran into a problem with regarding to a high side transformer fuse clearing time for SLG fault on the secondary of a transformer. Below is the information to my issue.
Transformer: 10000kVA, 67kV Delta-12.47kV Wye-Grounded, 7.13%
High Side Fuse: S&C 100E-SMD-1A Slow
SLG Fault on Secondary: 5519A
To my understanding, I though the high side fuse will only see ~58% of the SLG fault on the secondary of transformer for A-Phase and C-Phase due to shifting of transformer damage curve ([5519*(12.47/67)*0.58]=595.7A @ 67kV) . Based on 595.7A current, the S&C 100E-SMD-1A Slow will clear the fault at ~1.8112 seconds. However, I was told that the 1.8112 seconds clearing time is incorrect. And I was told that the fuse should clear based on the following current 1027A ([5519*(7.2/67*1.732)]) not 595.7A. Either I am not fully understand the concept or whatever I was being taught in school was incorrect. Please advise.
Thanks,
Transformer: 10000kVA, 67kV Delta-12.47kV Wye-Grounded, 7.13%
High Side Fuse: S&C 100E-SMD-1A Slow
SLG Fault on Secondary: 5519A
To my understanding, I though the high side fuse will only see ~58% of the SLG fault on the secondary of transformer for A-Phase and C-Phase due to shifting of transformer damage curve ([5519*(12.47/67)*0.58]=595.7A @ 67kV) . Based on 595.7A current, the S&C 100E-SMD-1A Slow will clear the fault at ~1.8112 seconds. However, I was told that the 1.8112 seconds clearing time is incorrect. And I was told that the fuse should clear based on the following current 1027A ([5519*(7.2/67*1.732)]) not 595.7A. Either I am not fully understand the concept or whatever I was being taught in school was incorrect. Please advise.
Thanks,