healyx
Electrical
- Apr 7, 2009
- 115
Hi,
Is the published total let-through energy (not pre-arc)for a fuse the largest amount of energy that a fuse will let-through for a fault in the adiabatic region (0-5s)? or is it just the worst case energy that will be let-through for the worst case fault level (e.g. device rating)?
I am looking at a gG 100A (rated 80kA) fuse that has a pre-arc let through of 14000 A^2S and total let-through of 65000 A^2S.
The device takes 5s to trip at 700A (end of adiabatic period). This equates to an I^2t let-through of 2450000 A^2S. This is higher than the published total let-through, but might be valid if the published total let-though only applies to the worst case fault. Which of these two do I use for the cable short circuit temp rise equation? Would any fault current limiting occur at only 700A? Peak current isn't altered for a fault that low according to data sheet.
I don't have access to BS88 or IEC60269-2-1 where I think the conditions for totla let-through are defined. Looking on the web, I suspect total let-through for a 100A fuse assessed at 4kA fault level.
Is the published total let-through energy (not pre-arc)for a fuse the largest amount of energy that a fuse will let-through for a fault in the adiabatic region (0-5s)? or is it just the worst case energy that will be let-through for the worst case fault level (e.g. device rating)?
I am looking at a gG 100A (rated 80kA) fuse that has a pre-arc let through of 14000 A^2S and total let-through of 65000 A^2S.
The device takes 5s to trip at 700A (end of adiabatic period). This equates to an I^2t let-through of 2450000 A^2S. This is higher than the published total let-through, but might be valid if the published total let-though only applies to the worst case fault. Which of these two do I use for the cable short circuit temp rise equation? Would any fault current limiting occur at only 700A? Peak current isn't altered for a fault that low according to data sheet.
I don't have access to BS88 or IEC60269-2-1 where I think the conditions for totla let-through are defined. Looking on the web, I suspect total let-through for a 100A fuse assessed at 4kA fault level.