What are the cons of protecting 5-60MVA power transformers with primary fuses? Why is the practice frowned upon?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
cuky2000 said:The typical minimum clearing time of a circuit breaker (including relay & CB interrupting time) is 2-3 cycles or larger. In contrast, fuses could trip within 1/2 cycles.
Mbrooke said:How does poorer protection present a disadvantage?
Cuky2000 said:4. Fuses are susceptible to aging degradation i) Fuses are subjected to gradual damage from heavy through faults, leading to an eventual fast trip for a low magnitude fault. ii) Fuses are not as precise in operating characteristics. Characteristics change slightly with temperature, pre-fault and loading cycles. iii) Moisture is recognized of one of the multiple stressor that can lead to failure. However, the predominant failure mode (80%)is attributed to the fatigue of the fuse link over long operation time due to exposure to elevated temperature, voltage transients, or short duration over current condition.
Bacon4Life said:I remember hearing some debate as to whether all three fuses need to be replaced anytime one of the fuses blows.
voltage transients
Single phasing causes very high negative sequence voltage and current and low voltages (Line-to-Neutral & Line-to-Line).