Here is the situation (in canada)...
The electrcian installed a squared 600v 60a switch with a 50A fuses. The switch feeds a 45kVA (80degc) 600V-208/120 transformer. The transformer feeds a 100A 120/208v squared panel c/w a 100a main.
The electrical safety authority says that because of rule 14-606 the primary fuses need to be changed to 40A and the secondary cables need to be upsized from #2 to #1.
Does the 100A breaker intergral to the panel board not count as suuffecient overload protection for the panel?
I do not understand...
Regards,
TULUM