Plinko

Electrical
Oct 29, 2001
12
Is anyone in this forum using the Elastimold 166FLR fused loadbreak elbows for sectionalizing light duty underground taps? If so, I would like to discuss the problems (if any) they've encountered in their application.
Please leave an email address or a contact number.
Thanks in advance.
 
Replies continue below

Recommended for you

I have use these at two utilities...
The newer fused elbows have fewer problems associated with the EPR materials from which they were made than did those manufactured 10 or 15 years ago. The older materials didn't seem to allow you to separate the two halves of the elbow / fuse housing following a fuse opration. The heat energy generated from the fault current apparently caused the housing to get a little sticky. We find that those made more recently are far easier to separate after a fuse operation, partially due to the materials used in their manufacture and partially due to an improved formulation for the silicon lubricant used to assemble the two halves of the housing.

One caution concerning the design of the fused elbow that you will need to keep in mind during re-fusing efforts: If either the test point or the tester you use on the test point to verify that the cable is de-energized happens to fail, then you have no positive method of verifying that the cable is dead and grounded. (We use test points, but we also require live-line tests to verify that a circuit is de-energized.) One option is to spike the cable going into the bottom half-housing to verify that the fused elbow is completely de-energized. Another option (we chose this one) is to install the fused elbow on 5-foot jumper whose remote end terminates in the same vault in which the fused elbow terminates. This way, you have visual verification of isolation from the energized circuit prior to changing the fuse.
 
Elastimold sells a low impedance meter to verify voltage for this product
 
Good point, edjh2. Those meters really do work pretty well. We have been able to make use of the low impedance meter in some situations where the high impedance meters we normally use won't work.

There have been a few rare instances where the test points didn't work and we were unable to pick up a reading even with the low impedance meter (old elbows), so we instituted the live-line test rule. By all rights the fused elbows are going to be newer and are not as likely to have test point problems, but we felt it was better to implement the live-line test (and the use of the jumper) across the board than it would be to wish we had in the wake of an electrical contact accident.
 