Hello again,
I have some 5kv switchgear (2 5kv fused S&C'c) that is to be used on a 2400v system. The spec says that we shall install medium voltage, general purpose, current-limiting fuses (5kv, Amp-trap, E-rated, CS-3 series fuses). The switchgear also has 3kv distribution class lightining arrestors on the line side of the switches.
My concern is that there are extra considerations that should be adhered to when specifying current limiting fuses of a higher voltage level on a lower voltage level (5kv on 2.4kv).
During a fault the current limiting fuses will produce a large resistance and hence a large overvoltage ESPECIALLY on a lower voltage system... (I believe this is because the fuse resistance is the same however, the fault current is usually more and hence the voltage transient is greater when a CL fuse is applied on a lower voltage than rated, please correct me if I am wrong
My question is (longwinded but..) how do I compare my lightning arrestor properties with that of the CL fuse properties under fault? What considerations are necessary when applying a CL fuse in this situation?
Regards,
Tulum
I have some 5kv switchgear (2 5kv fused S&C'c) that is to be used on a 2400v system. The spec says that we shall install medium voltage, general purpose, current-limiting fuses (5kv, Amp-trap, E-rated, CS-3 series fuses). The switchgear also has 3kv distribution class lightining arrestors on the line side of the switches.
My concern is that there are extra considerations that should be adhered to when specifying current limiting fuses of a higher voltage level on a lower voltage level (5kv on 2.4kv).
During a fault the current limiting fuses will produce a large resistance and hence a large overvoltage ESPECIALLY on a lower voltage system... (I believe this is because the fuse resistance is the same however, the fault current is usually more and hence the voltage transient is greater when a CL fuse is applied on a lower voltage than rated, please correct me if I am wrong
My question is (longwinded but..) how do I compare my lightning arrestor properties with that of the CL fuse properties under fault? What considerations are necessary when applying a CL fuse in this situation?
Regards,
Tulum