Gas pressure regulator venting

Status
Not open for further replies.

vannic

Mechanical
Sep 22, 2003
15
0
0
US
Anybody ever seen any references on how to size gas pressure regulator vents? We have boilers in the bowels of a large building that have regulators that need to be vented. We have medium pressure gas and using about 2500 CFH for each of 3 boilers. Any suggestions?
 
Replies continue below

Recommended for you

Vannic,

Vent lines on gas regulators are to be sized in case the diaphram in the regulator breaks. You want to be able to vent what is upstream of the regulator to a safe outdoor location in case this happens. This is to protect the downstrean equipment - you should also have a high pressure gas switch downstream of the regulator and shut off valve(s).

Some regulators come with internal over pressure relief valves and some application require either an internal or external over pressure relief valve.

In your case you have small boilers - my specialty is larger industrial applications. You might have to check with your local insurance company to get specifics - Factory Mutual might be of some help.


Good Luck!
 