Gas pressure
cme
I have gas fired equipment operating at 7-11" wg and I sized the pipe for 1/2 psig pressure drop. My question is what is one pound of gas equal to in inches wg? There is a regulator on the downstream pipe of the gas meter.
inches wg refers to inches water gauge -- and I am assuming that you mean psi (pounds per sq in) when refering to a pound of gas: use the standard formula 1" H20 = 0.5781 psi (when estimating I usually use a rule of thumb that 1" H20 is roughly equivalent to ½ psi -- recognizing that it is only a very rough estimate)
to answer your question: 1 psig = 1.7298 "H2O
With all due respect I think that pablo02 is mistaken.
1" psig does not equal 1.7298" H2O. 1 foot (12 inches) very approximately) is equal to 1 psig
1 psig is equal to 27.7" of water.
put another way
1" of water equals 0.0361 psig.
You can make these conversions very easily by remembering 4 numbers. Taking standard atmospheric pressure as the datum:
1 atmoshpere = 14.7 psig
1 atmosphere = 407" H2O
1 atmosphere = 30" of mercury
1 atmosphere = 101,325 Pascals or bars
therefore 1psig = 407/14.7 = 27.69" H2O
I agree in concept -- I should have left off the "g", my error (or added 'wg' to my answer) -- however, the question dealt with inches water gauge which is also a measurement above atmopheric pressure therefor the value is still valid if you disregard my error in units...
With all due respect,Accystan is correct -- I have used the wrong conversion factor (ounces/sq.in.)
My error -- glad that Accystan was watching -- as he points out the correct factor is 1" H2O = 0.0361 psi
(and my rule of thumb deals with inches Hg, not inches H2O)
My apoplogies...
No problem pablo02. Pretty good for an electrical guy.
Now. How many electrons are there in a cubic ohm.......?
Cheers
There are 2 in a cu ohm ...but if you let them out they become 8 because they are cubic ohms....I think!
0.5 inches water gage = 0.5 / 27.72 or
0.0180375 psi
1/2 psig = 27.72 / 2 = 13.86 inches water gage
I remember 1 cubic feet of water as weighing 62.34 lb
Therefore pressure excerted by a ft ht of water per sq in = 62.34/144 = 0.4329 psi
height of water column corresponding to 1 psi therefore = 1/.4329 = 2.31 ft = 27.72"