electricpete
Electrical
- May 4, 2001
- 16,774
This question concerns GE electromechanical motor protection relays which have a high-dropout trip in addition to the normal time overcurrent trip and instantaneous trip.
For example IAC66M described at:
Circuit diagram page 17.
The high-dropout trip is a separate instantaneous plunger element (50-1IOCB) set at 1.1*LRC (our setting) which picks up a telephone relay (50-1/OX) with 0.1 sec delay. After 0.1 seconds the telephone relay output NO contact will close to complete a path through the high-dropout-instataneous plunger contact 50-1IOCB (IF still closed) to energize a seal-in coil (T-SI) which closes/seals-in the trip output at pin 8.
In addition to the normal two flags for normal time overcurrent and instantaneous trip (bottom of the relay), there are two flags for the high-dropout at the top of the relay. One is driven mechanically by the plunger 50-1ICOB, and the other by the T-SI sealin relay.
I would expect that for any normal start, the starting current would exceed 1.1LRC during the initial quarter cycle due to dc offset, and then decay to LRC long before 0.1 seconds. I expect the result would be a single flag at 50-1/IOCB during every start (but no trip). We never see this flag.
Can anyone explain where I have gone wrong.
For example IAC66M described at:
Circuit diagram page 17.
The high-dropout trip is a separate instantaneous plunger element (50-1IOCB) set at 1.1*LRC (our setting) which picks up a telephone relay (50-1/OX) with 0.1 sec delay. After 0.1 seconds the telephone relay output NO contact will close to complete a path through the high-dropout-instataneous plunger contact 50-1IOCB (IF still closed) to energize a seal-in coil (T-SI) which closes/seals-in the trip output at pin 8.
In addition to the normal two flags for normal time overcurrent and instantaneous trip (bottom of the relay), there are two flags for the high-dropout at the top of the relay. One is driven mechanically by the plunger 50-1ICOB, and the other by the T-SI sealin relay.
I would expect that for any normal start, the starting current would exceed 1.1LRC during the initial quarter cycle due to dc offset, and then decay to LRC long before 0.1 seconds. I expect the result would be a single flag at 50-1/IOCB during every start (but no trip). We never see this flag.
Can anyone explain where I have gone wrong.