Anyone have any experience with application of GE 469 motor relay (or other digital relay) on the output of an AFD? It's replacing another digital relay that's been in service for a few years. CTs are on the drive output, but no PTs are available there (not surprising).
The FAQ from GE says this can be done if the CTs and PTs are on the drive output. But I can't see how the relay would get much useful voltage data out of the PWM output. I'm wondering if we could just bring in the line side bus PTs?
But GE doesn't give any advice on any adjustments required to the normal sine wave settings on the 469. I'm wondering if we can just set the relay thermal overload protection as we normally do, or if there are adjustments that need to be made.
A further complication is that there is a bypass contactor to allow running across the line and the 469 is in the circuit in both situations.