kelleyl

Mechanical
Nov 24, 2014
2
I am trying to design for a special shower drainage situation.
I have two showers that together drain 3gpm into a long shallow trench/depression in the floor to a 2" floor drain pipe, 5" square grate strainer.
The CPC says 2DFU for a floor drain, and 2DFU is the equivalent of 1gpm... So I am assuming that means my floor drain will only drain 1gal of water per minute.

So my question is does the shower in at 3gpm minus the drain out at 1 gpm equal 2gpm consistently collecting, or am I missing a key idea? Otherwise this seems it wouldn't work.

Any insight is appreciated!
 
Replies continue below

Recommended for you

The DFU to gpm correlation is general and used to predict flows on a statistical basis. A floor drain will drain more than 2 gpm, even at 2" outlet and 5" square. A 2" pipe at 1/8" slope will flow ~13 gpm before it becomes surcharged. Drains will likely flow more - so don't worry about overflows.
 