bdn2004
Electrical
- Jan 27, 2007
- 794
We have a small project to perform a power study for a new waste water facility. In the project documents they are specifying a new 750 kVA, 12.47-480V pad mounted, oil filled transformer. But they are NOT specifying new fuses in the HV terminal cabinet of that transformer. Is this the standard way this is done - rely on the Utility to provide the fuses for a transformer you own?
The construction is....a 12.47kV tap off the Utility pole line assuming Utility furnished cutouts on the pole, underground 50'+ 12.47kV cable -> 750kVA transformer -> 150' secondary conductors landing at a remote main circuit breaker inside the building.
(This seems odd too - is there not a tap violation here ? )
The construction is....a 12.47kV tap off the Utility pole line assuming Utility furnished cutouts on the pole, underground 50'+ 12.47kV cable -> 750kVA transformer -> 150' secondary conductors landing at a remote main circuit breaker inside the building.
(This seems odd too - is there not a tap violation here ? )