A radial line feeds an industrial site that has generation partially offsetting their load. Synchronizing equipment is at the generator breaker only. It is decided the sourcing substation should send a transfer-trip signal to the generator breaker when conditions dictate. Would you source this signal from a protective trip only, or include manual tripping as well?
Argument for including manual tripping: Any open might cause an island and possible out sych situation when the breaker is eventually manually closed.
Arguments for not including manual tripping: A sustained island is unlikely since load exceeds generation. The operator, knowing that generation exists down line, will be sure to contact the industrial site prior to closing. Fewer transfer-trip sources decreases the chance of an inadvertent generation trip.
Have I missed any arguments? What do the members here do? Thanks.
Argument for including manual tripping: Any open might cause an island and possible out sych situation when the breaker is eventually manually closed.
Arguments for not including manual tripping: A sustained island is unlikely since load exceeds generation. The operator, knowing that generation exists down line, will be sure to contact the industrial site prior to closing. Fewer transfer-trip sources decreases the chance of an inadvertent generation trip.