SolarPrestige
Electrical
- Mar 4, 2020
- 38
I have a generator which has a cubicle on each side, one called the line-side cubicle (LSC) and the other called the neutral-side cubicle (NSC). Just thinking about the LSC, it has connections coming in from the generator bushings and goes through to the isolated phase busduct on the other side. Inside it has busbars, voltage transformers (VTs or PTs), current transformers and surge arrestors. There are lots of joints, applied insulation and leads inside this box. The NSC is similar but with added neutral impedance equipment and with no surge arrestors.
Here’s the problem. We cannot undertake thermal imaging in these boxes. We do other routine inspections and tests but we cannot do the thermal imaging. One way to see the temperatures inside would be to take covers off and view while the generator is running, but we would not do this due to safety concerns. Another method is to install IR windows, but there may need to be a lot of these. Or we can just say low risk so let’s not worry about it. I don’t immediately like the do nothing answer, but installing windows would need a pretty good justification.
A flash over inside one of these cubicles would be a very high energy incident as the generator cannot be turned off instantly. There’s at least a big initial event from the generator and grid, followed by the generator winding its excitation down over some seconds while continuing to feed the fault current.
Has anyone seen issues with these types of systems related to incipient faults (e.g. poor joints, PD activity)? Anyone know about these systems failing?
And a related question, can EMI testing be used to find the same type of issues? How is an EMI test set attached to measure on this type of system? I am reading the Doble brochure for PDS200 and EMI-Surveyor and they say no physical connections on one and no HV connections on the other.
Thanks, Greg.
Here’s the problem. We cannot undertake thermal imaging in these boxes. We do other routine inspections and tests but we cannot do the thermal imaging. One way to see the temperatures inside would be to take covers off and view while the generator is running, but we would not do this due to safety concerns. Another method is to install IR windows, but there may need to be a lot of these. Or we can just say low risk so let’s not worry about it. I don’t immediately like the do nothing answer, but installing windows would need a pretty good justification.
A flash over inside one of these cubicles would be a very high energy incident as the generator cannot be turned off instantly. There’s at least a big initial event from the generator and grid, followed by the generator winding its excitation down over some seconds while continuing to feed the fault current.
Has anyone seen issues with these types of systems related to incipient faults (e.g. poor joints, PD activity)? Anyone know about these systems failing?
And a related question, can EMI testing be used to find the same type of issues? How is an EMI test set attached to measure on this type of system? I am reading the Doble brochure for PDS200 and EMI-Surveyor and they say no physical connections on one and no HV connections on the other.
Thanks, Greg.