I was recently called out to a hydro site that had an 8 MW, 6900V unit trip on A,B,C differential (Basler BE1-87G).
Within the neutral and phase CT's is a tap to a Static Exciter Transformer. Outside of the CT's, but still on the generator side of the Generator breaker is a surge pack, arresters, and PT's. On the buss side of the Generator breaker is a breaker for the Station service transformer(50/51 protection), a breaker for the tie to the grid through a 6900-11500v step up xfmr, and also a feeder breaker feeding a small camp load and aprox 5 miles of line to a headgate(50/51 protection).
All loads were being fed from the grid while generator was offline.
Assuming a generator problem since it tripped on differential, I tested the generator, CT's, and CT loops back to the relay. All was good.
Attempts were made to sync on to the buss, however it tripped instantly on 87, all three phases. It was then decided to try shedding all the load and disconnecting from the grid and energizing just a dead buss. This worked, and we were able to energize station service, and sync to grid. However when the feed to the small camp load and 5 miles of line was energized, the unit tripped on 87 all three phases.
I guess my question is how could a fault on this line trip all the way back to the differential protection of the generator? Also why were no problems apparent when this feeder was being energized from the grid.