Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Generator/Exciter S100 and S120 (ETAP)

Status
Not open for further replies.

sky2020

Electrical
May 21, 2019
39
0
0
CA
I am using ETAP to model a generator with an exciter?

I am trying to understand the effect of the S100 and S120 parameters of the generator.

etap-gen_imp_iy2mkx.jpg


What is the range of each of these two values? Do they differ between various software? How does it affect system performance?

So what about these values for the exciters? what is the range?

im_ed1xh2.gif


SE (FD1) Saturation at EFD1 [pu]
SE (FD2) Saturation at EFD2 [pu]
SE (VE) Exciter saturation function value at VE
 
Replies continue below

Recommended for you

S(1.0) and S(1.2) represents the value of saturation of synchronous machine at field voltage Efd of 1.0 and 1.2 p.u., respectively. These are the degree of saturation of the machine and how far it deviates from the air gap line of the machine. If you like more information about these, please have a look on open and short-circuit characteristics of synchronous machines.
 
Status
Not open for further replies.
Back
Top