srm01
Structural
- Apr 6, 2022
- 10
I was at a jobsite yesterday and the generator exhaust pipe was running close to/touching the concrete beam overhead. See attached pictures. There is maybe 1/2" thick insulation wrap around the pipe. I have reviewed the Florida Building Code and NFPA37 for guidance on this and the most applicable statement I could find is from NFPA37 which states "Exhaust pipes and ducts shall have clearances of at least 9 in. to adjacent combustible materials...". However, concrete is not combustible and there is no mention of clearance to non-combustible materials. The generator max exhaust temp is 920F.
I am not concerned about the beam catching fire, but what about the heat transfer into the beam and potential adverse effects from that and thermal cycling? Has anyone encountered this and is it addressed anywhere?
The beam is 33"H x 36"W.
Thank you in advance for your input!
I am not concerned about the beam catching fire, but what about the heat transfer into the beam and potential adverse effects from that and thermal cycling? Has anyone encountered this and is it addressed anywhere?
The beam is 33"H x 36"W.
Thank you in advance for your input!