generator fault current 2

Status
Not open for further replies.

ksreddy35

Electrical
Aug 11, 2008
6
please let me know the fault current calculation of generator of 20 to 50 MW.
 
Replies continue below

Recommended for you

Hi.
For the start:
I3ph-fault=Inom gen/X"d (for the turbogenerator from 13%-17%).
Regards.
Slava
 
Thank you for your reply,

For 30MW 11KV Generator, rated current is 1968, Xd"(sat)-11.84% & Xd"(unsat)-14.79. i have to take saturation value or unsaturation value of Xd".
 
Hi.
You have use saturated transient X"d 11.84%
Regards and Good Luck.
Slava
 
hi

you informed as below

For the start:
I3ph-fault=Inom gen/X"d (for the turbogenerator from 13%-17%).

but i have still one doubt i,e I nom gen (or) V nom gen.
 

It is Inom in ampere and X"d in %

So I3ph = 1968/(11.84/100)
 