aillas
Mechanical
- Apr 12, 2006
- 2
Hi all,
My house is power supplied by a diesel generator. The load is purelly single phase, so basically
never balanced as AC`s are starting and stopping at any time. It is not uncommun to measure 20
Amps on the neutral in this situation. The fact is the generator as difficulties to maintain the
frequency at 50Hz (the standard here). The frequency frequently drops below 45Hz damaging equipments
or switching on the UPS.
I have two hypothesis for that. I observed that the generator is not grounded so I guess it is more difficult for
the DVR to find its balance. As it is frequency/load related I also suspect the governor.
Here are my questions:
1. For the grounding of the neutral. Can I proceed and ground the neutral even with such currents (20A) in it.
2. I am correct to suspect the governor?
3. Any references or online reading on the above subjects so I could go further in my learning of the problem
Thanks and regards.
My house is power supplied by a diesel generator. The load is purelly single phase, so basically
never balanced as AC`s are starting and stopping at any time. It is not uncommun to measure 20
Amps on the neutral in this situation. The fact is the generator as difficulties to maintain the
frequency at 50Hz (the standard here). The frequency frequently drops below 45Hz damaging equipments
or switching on the UPS.
I have two hypothesis for that. I observed that the generator is not grounded so I guess it is more difficult for
the DVR to find its balance. As it is frequency/load related I also suspect the governor.
Here are my questions:
1. For the grounding of the neutral. Can I proceed and ground the neutral even with such currents (20A) in it.
2. I am correct to suspect the governor?
3. Any references or online reading on the above subjects so I could go further in my learning of the problem
Thanks and regards.