Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Generator grounding & protection with a wye-wye transformer 4

Status
Not open for further replies.

choi1167

Electrical
Dec 14, 2005
28
Given a generator 1.6MW 480Y/277V 60Hz and a GSU transformer with primary and secondary windings wye connected, neutral internally tied and solidly grounded.
What is the best method of grounding and minimum protection (relaying) necessary for the generator?
 
Replies continue below

Recommended for you

[blue]The enclose information is a summary from the Special Report of the IEEE Relay Committee regarding the application of generator grounding resistor interacting with a generator step-up transformer (GSU) in YG-YG winding configuration serving local load and interconnected with an utility substation.

I hoping this information help enlighten this discussion in benefit of the project and the member of this forum.

Good luck all. [/blue]

AP, PE

Generator_Gnd1_XFMR_YG_YG.jpg
 