Electricpete's question on motor rewinds jogged me to ask this question to the group:
For an ac turbo-generator (approx 20 MVA) that has been rewound (stator)and given a higher kVA rating, what should be used for generator reactances?
We have the reactance data and time constants for the original generator from the manufacturer.
In the absence of any other available data, is it reasonable to assume that the ohmic values of reactance will not change too much and just recalculate the generator reactances in percent based on the new kVA rating? This seems reasonable to me since the stator core has not been changed, slot geometry is unchanged, and increase in kVA rating is likely due more to better winding insulation than anything else.
We are trying to get an answer on this from the manufacturer (who also did the rewind, but just trying to think through it logically.
For an ac turbo-generator (approx 20 MVA) that has been rewound (stator)and given a higher kVA rating, what should be used for generator reactances?
We have the reactance data and time constants for the original generator from the manufacturer.
In the absence of any other available data, is it reasonable to assume that the ohmic values of reactance will not change too much and just recalculate the generator reactances in percent based on the new kVA rating? This seems reasonable to me since the stator core has not been changed, slot geometry is unchanged, and increase in kVA rating is likely due more to better winding insulation than anything else.