I anm trying to figure out what is good utility practice for performing generator interconnection studies on distribution systems. I have a situation where there is so much generation on the distribution system that there is a concern about backfeeding to the transmission level and overloading the distribution transformer (115/33kV).
The utility is using spreadsheet to deteremine the loading on the transformer. They just totaled up the maximum capacity for all of the generators (no historical factor or diversity factor) and then subtracted the minimum load. They also did not include any losses or run a power flow analysis to include those losses in calculating the bank loading.
1) Please me know if you would include the losses and/or us a power flow program to do this analysis.
2) Would you use historical factors or diversity factors for the existing generation?
Thanks!
The utility is using spreadsheet to deteremine the loading on the transformer. They just totaled up the maximum capacity for all of the generators (no historical factor or diversity factor) and then subtracted the minimum load. They also did not include any losses or run a power flow analysis to include those losses in calculating the bank loading.
1) Please me know if you would include the losses and/or us a power flow program to do this analysis.
2) Would you use historical factors or diversity factors for the existing generation?