ECpower
Electrical
- Jan 14, 2014
- 2
The factory default on an Easygen 3000 for generator load unbalance is 15%. Our generator is set up to load share with the utility. We have a fused capacitor bank on the load side of the utility recloser. Gen set is 2mw and the load runs below 700kw. Cap bank has(3)200kvar units, one per phase and wired in a wye configuration. During system startup we had issues with one of the CTs which was open circuited. When the CT failed the capacitor fuse blew as well. Since then, the fuse has been replaced and the system is back up and running. My question is what the maximum recommended %current unbalance for a gen set should be. The default generator protection will not allow the system to run beyond 15% imbalance. Can this be set higher so that a blown capacitor fuse won't shut us down when the utility goes down?
I guess part of the answer will depend how much the current imbalance effects the bus voltage. We haven't tested yet but let's assume it won't change over 3-5%.