Nfpa 110 (standby generators states you must meet 30% of your rated generator load
every month. If not you must perform a load bank ,and the requirement is,
25% for one half hour 50% for next half hour and 75% for the last hour.(KW name plate)
The vender we use uses a resistive load bank. The question I have is would it be calculated with a .1 power factor as apposed to a .8 power factor?


 
Replies continue below

Recommended for you

.1 power factor? How do you get that out of resistive load bank?
 
Load is measured in Watts (or kW etc.)
The reactive component does not present any loading on the prime mover.
Use generator kW rating and load bank kW loading.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
resistive load banks are unity PF so you need to calculate at 1.

When an elephant is in trouble even a frog will kick him.
 
Thank you all for your input.
My suspicions are correct,
I am only a master electrician
and just needed to verify with
others, thank you all.
 