Hi,
I am currently working on an Areva Micom P342 generator protection relay.
I am have some difficulties and I was hopeful that someone here may be familiar with these relays or generator protection relays in general.
1) Must voltage or resistor always be connected to the Vneutral terminals C23, C24?
2) Should the any/all protection functions isolate the prime mover as well as the generator. Prime mover is a DC motor.
3) The generator is small 2kW. And produced a nominal current of 2-4 amps. Could it damage the relay connecting this current direct to the CT terminals without a CT?
4) Similar the nominal voltage is rated at 220V. I had planned using 3 standard 2:1 single phase transformers connected in delta. Would there be any problem with this?
I am currently working on an Areva Micom P342 generator protection relay.
I am have some difficulties and I was hopeful that someone here may be familiar with these relays or generator protection relays in general.
1) Must voltage or resistor always be connected to the Vneutral terminals C23, C24?
2) Should the any/all protection functions isolate the prime mover as well as the generator. Prime mover is a DC motor.
3) The generator is small 2kW. And produced a nominal current of 2-4 amps. Could it damage the relay connecting this current direct to the CT terminals without a CT?
4) Similar the nominal voltage is rated at 220V. I had planned using 3 standard 2:1 single phase transformers connected in delta. Would there be any problem with this?