VTArch
Specifier/Regulator
- Mar 3, 2016
- 3
Hi All,
What if any is the Fire Resistance Rating for a room enclosing an Emergency Power Supply (Generator Room) in a parking Garage (including Code references Please).
I am currently look at:
NFPA 110 Chapter 7, 7.2.1.1 requires the Emergency Generator room to be in a 2 hour enclosure.
NFPA 37 4.1.2 Seems to say, a generator in a Parking Garage does not need fire protection to enclose a generator, BUT if it is enclosed, it should be an min. 1 hour rating.
"The current reading suggests the diesel generators provided in parking garages do not need to be protected by fire restive construction".
See P.3 of 6.
I have looked at thread184-374872 & thread179-365200 on this forum to no avail.
Thanks!