There are several 400v generators connected to a 400/11,000v YnYn transformer. The 11kv system supplies some industrial plant. It is a separate system with no utility.
The 11kv transformer neutral is solidly grounded.
The generator neutrals are connected to an LV neutral bus, with one connection to ground.
We would normally expect a delta winding on the 400v, so I'm not sure how the 400v transformer neutral should be connected.
a) Left unconnected.
b) Connected to the LV neutral bus with the generators.
c) Other