KAA
Electrical
- Jul 4, 2002
- 3
Hi
The following generator is available at a particular site
Generator rating 300KW (375 KVA) , L-L Voltage 380V, L-N Voltage 220 V, Power factor 0.8, Current at 0.8 pf is 570A, Frequency 60Hz, 3phase 4 Wire System
The generator is provided with the following calibrated instruments with Recorder to check the performance
a) Generator Output Voltage
b) Generator Output Current
c) Generator Output Frequency
Only Resistive load bank is available
The following additional Test is to be undertaken to check its performance. " Transient Voltage Regulation at rated speed at 0.4power factor"
To achieve the requirement the following step was to be done
1) Step down load to 71% of KVA
The recorder shall state the recovery time which is actually required.
Kindly provide details on the calculation of the Load or load current to be considered and how to achieve the result required by the client. Your help would be highly appreciated
The following generator is available at a particular site
Generator rating 300KW (375 KVA) , L-L Voltage 380V, L-N Voltage 220 V, Power factor 0.8, Current at 0.8 pf is 570A, Frequency 60Hz, 3phase 4 Wire System
The generator is provided with the following calibrated instruments with Recorder to check the performance
a) Generator Output Voltage
b) Generator Output Current
c) Generator Output Frequency
Only Resistive load bank is available
The following additional Test is to be undertaken to check its performance. " Transient Voltage Regulation at rated speed at 0.4power factor"
To achieve the requirement the following step was to be done
1) Step down load to 71% of KVA
The recorder shall state the recovery time which is actually required.
Kindly provide details on the calculation of the Load or load current to be considered and how to achieve the result required by the client. Your help would be highly appreciated