we have a power system with 132 kV/11 KV YYnd0 , 20 MVA Transformer and two TG's 12 MW and 16 MW connected to 11 kV with resistance earthing 400 A thro NGR.
Now we want to add additional 22 MW TG at the 11 kv level.In order to isolate the earthing of new TG it is proposed high impedence earthing thro NGT/NGR and an Isolation transformer 11 kV/11 KV with Ddo .
There are additional proposal to consider the Generator transformer with Dyn11 earthing , in this case the new TG -22 MW will supply the entire power hence the earthing is needed at the 11 KV level. Now is it possible to synchronise the new TG 22 MW with Gen. Transformer, Dyn 11 vector group with the grid transformer 20 MVA YYnd0. There is a argument that the generator source is 0 degree vector so it is possible to synchronise with the grid.
ESW,
Now we want to add additional 22 MW TG at the 11 kv level.In order to isolate the earthing of new TG it is proposed high impedence earthing thro NGT/NGR and an Isolation transformer 11 kV/11 KV with Ddo .
There are additional proposal to consider the Generator transformer with Dyn11 earthing , in this case the new TG -22 MW will supply the entire power hence the earthing is needed at the 11 KV level. Now is it possible to synchronise the new TG 22 MW with Gen. Transformer, Dyn 11 vector group with the grid transformer 20 MVA YYnd0. There is a argument that the generator source is 0 degree vector so it is possible to synchronise with the grid.