As an example of what can happen when you do something the designer did not expect:
Some years ago I was running the site acceptance test on a small gas turbine generator set
The set tripped on an external fault, we allowed it to get to standstill and immediately, I then pressed the start button. The set began pre purge and started to crank. It reached firing speed, gas valves opened, NO IGNITION, my fist hit the emergency stop button so hard that you could still see the mark on my fingers the next day!
Subsequent investigation revealed that the ignition was turned off by sensing the power turbine gas temperature. As the turbine was still hot from the earlier run, the temperature was still hot enough to hold off the ignition.
The turbine application engineers told us "but you should not restart until the post lube pump has run and timed out - 30 minutes.... This will give sufficient time for the turbine space to cool below ignition hold off."
There was nothing in the application manual about this!
Admittedly, the controls were basically an electromechanical system, and nowhere near as comprehensive as today's monitoring systems. It does show that one should exhibit caution when operating outside design parameters.