Generator Underexcitation Relaying

Status
Not open for further replies.

HamburgerHelper

Electrical
Aug 20, 2014
1,127
How bad is it to have 40 elements with 0.5-0.6 second tripping times for large units? How quickly does tripping need to happen during an under excitation event to avoid damaging the unit?

------------------------------------------------------------------------------------------
If you can't explain it to a six year old, you don't understand it yourself.
 
Replies continue below

Recommended for you

0.6s delay is no issue.
The delay could even be 2s to avoid unnecessary trip of generator on '40' during a grid fault condition.
It is also a practice to wire under excitation coupled with under voltage for instantaneous trip.

Rompicherla Raghunath
 