Remote facility with four 4160V 2600kW generators in parallel. All gen's each have a NGR on the neutral. There is voltage imbalance of 6%, regardless of which or how many generators are running, with zero load. The bus line-to-line voltage is equal (4.15kV) but the line-to-neutral varies (2.3kV for phase A, 2.6kV for phase B, and 2.5kV for phase C, roughly).
Each generator has Y connected PT's on the 4160V side, right at the stator connections. This MAY cause some circulating currents if the Y connected PT neutral is grounded, but it shouldn't cause a floating neutral.
The common bus has a DELTA-WYE PT. Both PT's (bus and each generator PT) show the same imbalance.
All NGR's have been inspected to ensure continuity to ground.
A couple points... The voltage imbalance is apparent regardless if gen 1, 2, 3 or 4 is on, and is apparent whether there is no load (all feeder breakers open on the common bus) or any value of load on (1200kW load bank and/or plant load).
Having a tough time finding where the floating neutral is coming from. Anybody have some ideas?
Each generator has Y connected PT's on the 4160V side, right at the stator connections. This MAY cause some circulating currents if the Y connected PT neutral is grounded, but it shouldn't cause a floating neutral.
The common bus has a DELTA-WYE PT. Both PT's (bus and each generator PT) show the same imbalance.
All NGR's have been inspected to ensure continuity to ground.
A couple points... The voltage imbalance is apparent regardless if gen 1, 2, 3 or 4 is on, and is apparent whether there is no load (all feeder breakers open on the common bus) or any value of load on (1200kW load bank and/or plant load).
Having a tough time finding where the floating neutral is coming from. Anybody have some ideas?