a friend asked me a question:
In the generator test, the voltage between phase and zero was measured
400,400,230
What could be the problem?

thanks
 
Replies continue below

Recommended for you

It seems Blue phase terminal and star point (neutral terminal) got interchanged it looks.
It could be in the generator terminal box.

Rompicherla Raghunath
 
Operator error.
A-B = 400 Volts
A-C = 400 Volts
A-N = 230 Volts.
The tester inadvertently interchanged one phase and the wye point when testing.
Instead of testing from neutral to A, B, and C he tested from A to B, C, and neutral.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
hi
Further to the question I asked:
Regarding to the attach drawing if I change the connection between points 9 and 12 this mean the star point (4,8,9)
What tensions will I measure between the phases and and neutral
L1-N
L2-N
L3-N

thanks
 
 http://files.engineering.com/getfile.aspx?folder=e86523fd-b30e-46da-b7cb-7ef31875f558&file=v1-09_Section_07_Generator.pdf
Tiredly, 230 V, 230 V and 230 V.
Se my previous post.
To see 400 Volts you are measuring phase to phase. A-B, and A-C. To see 400 Volts from two 230 Volt windings the phase angles are correct.
Your friend had one phase interchanged with the neutral when he took his measurement.


Bill
--------------------