mbk2k3
Electrical
- Nov 18, 2010
- 97
Hey folks,
I have 3x 13.8kV generators connected in parallel to a 13.8kV bus with a zig-zag transformer.
I'm trying to see what my options are here for the generator neutrals. See attached PDF for a sketch of what I'm trying to get at.
The way I see it I have 3 options: OPTION 1 - transformer in neutral, OPTION 2 - transformer with resistor, OPTION 3 - full blown NGR
[ol 1]
[li]What do I do with the generator neutrals to achieve quick tripping + selectivity?
[/li]
[/ol]
I have 3x 13.8kV generators connected in parallel to a 13.8kV bus with a zig-zag transformer.
I'm trying to see what my options are here for the generator neutrals. See attached PDF for a sketch of what I'm trying to get at.
The way I see it I have 3 options: OPTION 1 - transformer in neutral, OPTION 2 - transformer with resistor, OPTION 3 - full blown NGR
[ol 1]
[li]What do I do with the generator neutrals to achieve quick tripping + selectivity?
e.g. If G2 has an internal ground fault, I want the ground fault current to be limited and only G2 to trip.
e.g. If the 13.8kV bus has a fault, I want all 3 generators to trip offline.[/li]
[li]NGRs (OPTION 3) at 13.8kV becomes big and expensive. Can I avoid NGRs and stick to a single phase PT/grounding transformer with a resistor connected (OPTION 2) to limit the fault current?[/li]
[li]OPTION 1 would result in transient overvoltage conditions + ungrounded arcing ground fault condition after the generator breaker opens, no?[/li] [/ol]